How much refrigeration do I need for my homebrew keg cabinet

I have constructed a keg cabinet as part of my bar in my basement and am trying to figure out how much refrigeration I need to keep my kegs cool. The cabinet measures 27" H x 40" W x 24" D and has 1.5" of pink Styrofoam insulation board on all sides. I read Chris Bible’s article in this month’s BYO and calculated that I need about 400 BTU/Hr to keep the interior at about 35 deg F with an exterior temperature of about 75 deg F but this seems like a low number. Can anyone tell me if this value is in the right ball park? Also, I am trying to decide whether to use conventional refrigeration or thermoelectric. For conventional, I am looking at a remote condenser unit off to the side with an evaporator inside the cabinet. A thermoelectric unit could be mounted directly to the side of the cabinet. Any thoughts on pros and cons of each type of system?  Can anyone suggest a unit that can provide the level of cooling that I need at the above temperatures.

Thanks.

I’m all for using a TEC system, but my experiences with them have been mixed. Cools well but keeping a stable temp was problematic. Zymurgy has the article about the Ghettochill 9000 with two TECS and a power supply.

Yes, I read the article in Zymurgy as well and went back and read the article on the Gettochill 5000 in last year’s gadgets issue but I didn’t see any info on how to choose a unit of the correct size.  I did a little research on thermoelectric units and it looks like they become less and less efficient the larger the temperature differential you are trying to achieve.  If I was interpreting the information correctly, I looked like I would need a 1500 BTU unit to pump 400 BTU/Hr at a 40 deg F differential.

Not much help with your engineering issue, but I did notice you said 35º…IMHO waaaayyyy too cold. 45 is the highest I can set my keggerator, and it would be on 50º if I could. Cold kills flavor.

If you want someone to check your math, you have to give the r-value for the insulation.

I looked online and found that the R value for the foam ranges between 4 and 8 per inch of insulation so I used a value of 4.

I know that 35 is colder than I really want to keep my beer but I want some factor of safety so the unit wont have to run all the time.  The cabinet is actually devided into two compartments and I want to be able to keep my lagers and lighter ales at about 40 deg in one compartment and my heavier ales at about 50 deg in the other.  I plan to use thermostaticaly controlled fans to draw cold air from the colder compartment to the warmer.  I just want to make sure that, if anything, I have more refrigeration than I need rather than less.

OK, so the area is 274024 = 25920 in^2 = 180 ft^2. Going with an r-value of 4.0 ft^2-°F-hr/BTU-in:
(180 ft^2)(40°F)/(1.5 in)(4.0 ft^2-°F-hr/BTU-in) = 1200 BTU/hr.

The cold sinks shed a lot of condensation so you might consider this in you decision.

I am confused, 27" = 2.25 ‘, 40" = 3.33…’ and 24" = 2’

so volume is 2.253.332 = ~15 cubic feet rather than 180. am I missing something?

No, but I am because we want surface area, which is (22740)+(24024)+(22427) = 5376 in^2 = 37.33 ft^2. And the power required is 249 BTU/hr.

Apparently I shouldn’t have done that late at night.

ahh cool, well as long as we are wrong. :wink:

Sorry.  I’m new to this forum stuff so I don’t know how to quote who I’m responding to but 249 BTU/hr is the same number I got.  I just thought I might me plugging in a number in with the wrong units somewhere.  I bumped it up to 400 to account for leakage and so the unit wouldn’t have to run all the time.  Since we’re all coming up with the same number, what I need to know now is what kind of refrigeration unit I need to provide that rate of cooling.  I’ve looked at a unit designed for boats manufactured by Mermaid, the MM2 remote refrigeration unit with their 425M evaporator, but I didn’t see a BTU rating on their web page.  I’ve also looked at a 1/4 HP Embraco condensing unit which is rated at 3650 BTU [u]http://www.globalindustrial.com/p/hvac/compressors-line-filter-dryers/compressors/embraco-condensing-unit[/u] but that seems like way more than I need.  I also found a Dayton unit (CU102 Commercial Temperature Air Condensing Unit) [u]http://www.daytonrefrigeration.com/servlet/the-163/dayton-refrigeration%2C-refrigeration-parts%2C/Detail[/u] but again the BTU rating seems way more than I need.  What I’m not sure of is how the rated capacity applies at the temperature differential that I am looking for, especially after discovering how much the TEC units drop off with temperature differential.  I’m hoping someone with some refrigeration experience and/or knowledge can give me some guidance on how large a unit I need to pump 400 BTU per hour at a 40 deg F differential.  I would prefer a TEC unit because of he simplicity of installation but the efficiency issue may make that unfiesable.  Any guidance would be greatly appreciated.

I know people have done something similar to what you want, although on a larger scale, using a window air conditioner. That might be the cheapest and/or easiest option. Any commercial unit should be overkill for what you need.